I am travelling and can't cite the section from memory, but in Chap. 5 it says 
that you can take an additional floor with a 13R in R-1 occupancies.  
Otherwise, you can't take modifications or exceptions with residential 
sprinkler systems.
 
Steve L.

________________________________

From: [EMAIL PROTECTED] on behalf of John Drucker
Sent: Thu 3/22/2007 10:10 AM
To: [email protected]
Subject: RE: trade-offs and 13R and where in the IBC



Gregg,

I'm not familiar with the CBC, however lets see if there's an equivalent
to IBC 903.1.2, Residential Systems " Unless specifically allowed by
this code, residential sprinkler systems installed in accordance with
NFPA-13D or NFPA-13R shall not be recognized for the purposes of
exceptions or reductions permitted by other requirements of this code".

I think that sums it up.

John

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg
Fontes
Sent: Thursday, March 22, 2007 11:58 AM
To: [email protected]
Subject: RE: trade-offs and 13R and where in the IBC

John,
The 2001 CBC sections 505 & 506 state "that the area & floors can be
increased if an approved automatic sprinkler system is provided
throughout."
(Both sections do have exceptions where this does not apply.)  These
sections do not specify what an approved automatic sprinkler system is.
This is where the confusion comes in.  What is the codes definition of
an approved automatic sprinkler system?  2001 CBC Chapter 9 does not
specify a definition for an approved automatic sprinkler system.  It
just defines Automatic Fire Extinguishing System as "an approved system
of devices and equipment that automatically detects a fire and
discharges an approved fire-extinguishing agent onto or in the area of
the fire."  So what is an approved automatic sprinkler system?

Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Thursday, March 22, 2007 8:52 AM
To: [email protected]
Subject: RE: trade-offs and 13R and where in the IBC

Gregg, pulled the trigger too fast.

Chapter 9 provides the differentiation for fire sprinkler systems,
specifically  903.3.1.1 (NFPA 13), 903.3.1.2 (NFPA 13R) and 903.3.1.3
(NFPA 13D)

John

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Thursday, March 22, 2007 10:39 AM
To: [email protected]
Subject: RE: trade-offs and 13R

Gregg,

Heres the references;

2000 IBC

504.2 Automatic Sprinkler Increase Height which includes special
provisions for 903.3.1.2 (13R) Systems.

506.3 Automatic Sprinkler Increase Area

Table 601 Note d. Fire Resistance Rating Reduction including prohibition
on "doubling up".

I don't have the 2006 handy, but I can provide those references as well.

Hope that helps,

John Drucker
Fire Protection Subcode Official
New Jersey


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg
Fontes
Sent: Thursday, March 22, 2007 10:13 AM
To: [email protected]
Subject: RE: trade-offs and 13R

I was just asked this questions by an architect.  Where in any building
code does it state trade-offs for 13 or 13R system?  Where does it
define the system type for trade-offs?  I know it states fire
sprinklers, but does it state the system type anywhere? 

Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, March 22, 2007 7:46 AM
To: SprinklerFORUM
Subject: trade-offs and 13R

As part of the thread on 13D in row houses, a comment was made about
trade-offs driving the system type to a full 13 system.  Since many of
us are ingrained with the old requirement that trade-offs require a full
13 system, I wanted to emphasis that MOST design aspects in a 
residential facility are now allowed trade-offs with a 13R system.  
The primary aspect that is restricted to a full 13 system is area
increase.  Even building height can be increased with a 13R.

Roland
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to