1987 13, section 5-2.3.1 "Gridded dry-pipe systems shall not be installed."
1985 13, section 5-2.3.1 "Not more than 500-gal system capacity for gridded
systems or not more than 750-gal system capacity for non-gridded systems..."


----- Original Message ----- 
From: "Jimmy Waite" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, March 26, 2007 3:50 PM
Subject: RE: Mezzanine Calcs.


> Yep, a dry grid.  Apparently it was allowed before the '88 edition of 13.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Gary Stites
> Sent: Monday, March 26, 2007 2:51 PM
> To: [email protected]
> Subject: RE: Mezzanine Calcs.
>
>
> Dry Grid?
>
> Gary Stites
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Todd
> Williams - work
> Sent: Monday, March 26, 2007 1:45 PM
> To: [email protected]
> Subject: Re: Mezzanine Calcs.
>
> Jimmy,
>
> If it were me, I'd do the calc. Since you are tying into the gird, you
> are not maintaining a pipe schedule back to the riser so you can't
> really call it pipe schedule. Plus, you might be amazed at the amount of
> friction loss that can be generated when you calc through a grid to a
> single point to feed a tree system.
>
> Todd
>
>
> At 03:53 PM 3/26/2007, you wrote:
>
> >Dear Forum,
> >
> >We are currently working on a project where we are tying onto a dry,
> >gridded sprinkler system, installed in 1985.  There are two existing
> >dry systems and they each cover an area of about 13,100 square feet.
> >The lower floor is a tree system that was sized by "Table 3-7.1" of
> >NFPA 13, 1984 Ed.  The main floor is a grid that was designed at a
> >.275/ 3000 square feet with 500 gpm hose allowance.  The addition that
> >we are sprinklering is only 2,000 square feet.  On the main floor of
> >the addition there is a mezzanine of about 1,000 square feet.  Is a
> >calculation even needed for such a small addition, or can we use the
> >existing pipe sizing as our guide?  If a calculation is required, would
>
> >we calculate the sprinklers along the roof deck by themselves, or do we
>
> >need to include the sprinklers under that mezzanine in our calculations
> as well.
> >
> >Thanks for the help
> >
> >Jimmy Waite
> >Burtell Fire Protection, Inc.
> >[EMAIL PROTECTED]
> >406-652-7697
> >
> >
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> 860-535-2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to