Let me start by saying I've only been in the sprinkler world for just over a
year so if any thing I ask is "rookie-ish" please keep that in mind. I'm
looking for ideas that some of you may use when starting a new project when
it comes to selecting what heads (head spacing) to use. For example: I am
starting a retail store (mercantile) that has a Static of 47 psi Residual of
42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is
take the density x area of operation x 1.4 (for overage) + hose allowance.
That gets me roughly the system gpm demand. So .20 x 1500 = 300 x 1.4 = 420
+ 250 (hose) = 670 gpm. I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi. From
that psi I take out for the BFP, elevation, 40% (friction loss & etc) and
whatever is left I find a head with an end head pressure that's slightly
under that and away I go.... Any thoughts? Suggestions? Better Ideas?
Regards,
Brian Harris
First Defense Fire Protection
<mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum