You've basically done it in your post.  Though the 40% for overage seems
to be a little off.  I will use 15 to 20% max.  Any more than that means
your branch lines are probably well undersized.

Jamie Seidl
Affordable Fire Protection, Inc.
Project Manager
P - (800) 862-7860
F - (704) 892-0157

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 9:52 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System

I'm looking for a way to take the given information (static, residual,
flow) for a given job and come up with a head spacing (standard or
extended
coverage) that will work.

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 27, 2007 9:46 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System

I don't know if this is what you are looking for, but if you use a
sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to
minimize pressure demand) is 106 square feet.  Maybe a 10 x 10.5 foot
spacing. 

The approach that you take will differ depending upon the ALL of the
factors associated with the project.  A holistic approach to each
project is needed.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 8:35 AM
To: [email protected]
Subject: Selecting Heads For a New System

Let me start by saying I've only been in the sprinkler world for just
over a year so if any thing I ask is "rookie-ish" please keep that in
mind. I'm looking for ideas that some of you may use when starting a new
project when it comes to selecting what heads (head spacing) to use. For
example: I am starting a retail store (mercantile) that has a Static of
47 psi Residual of
42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand.  So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm.  I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From
that psi I take out for the BFP, elevation, 40% (friction loss & etc)
and whatever is left I find a head with an end head pressure that's
slightly under that and away I go.... Any thoughts? Suggestions? Better
Ideas? 

 

           Regards,

              Brian Harris
First Defense Fire Protection


   <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax



 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to