I'd note that 40% overage is pretty HUGE. 10% is more like it, especially since your water supply won't allow you to be aggressive on pipe sizes- which wiould accentuate overdischarge. Bet you'll be less than 10% unless it's a tree system- which would have more OD than a gridded system.
Might I suggest AFSA and NFSA for some Boot Camp lessons? You'll learn a LOT faster, and -at least IMHO- it's far better to learn thru education than to learn by making mistakes. glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Tuesday, March 27, 2007 9:46 AM To: [email protected] Subject: RE: Selecting Heads For a New System I don't know if this is what you are looking for, but if you use a sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to minimize pressure demand) is 106 square feet. Maybe a 10 x 10.5 foot spacing. The approach that you take will differ depending upon the ALL of the factors associated with the project. A holistic approach to each project is needed. Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, March 27, 2007 8:35 AM To: [email protected] Subject: Selecting Heads For a New System Let me start by saying I've only been in the sprinkler world for just over a year so if any thing I ask is "rookie-ish" please keep that in mind. I'm looking for ideas that some of you may use when starting a new project when it comes to selecting what heads (head spacing) to use. For example: I am starting a retail store (mercantile) that has a Static of 47 psi Residual of 42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is take the density x area of operation x 1.4 (for overage) + hose allowance. That gets me roughly the system gpm demand. So .20 x 1500 = 300 x 1.4 = 420 + 250 (hose) = 670 gpm. I then plot that gpm on my water supply curve (N1.85) to get the psi for that gpm; in this case that's around 45psi. From that psi I take out for the BFP, elevation, 40% (friction loss & etc) and whatever is left I find a head with an end head pressure that's slightly under that and away I go.... Any thoughts? Suggestions? Better Ideas? Regards, Brian Harris First Defense Fire Protection <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum