Signage is required by NFPA 30, and the color may come from OSHA, as in "Shall be Bright and easily recognizable" and somewhere else OSHA says "Red or Yellow, to indicate the appropriate hazard---" Down Under may not have the same types of wording.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Loren Johnson" <[EMAIL PROTECTED]>
To: <[EMAIL PROTECTED]>
Sent: Friday, April 13, 2007 11:24 AM
Subject: Re: Flammable liquid storage cabinets in retail stores


I had this situation come up on previous jobs.  In
checking with local AHJs, OSHA, and the like, it was
indicated as long as the cabinet is an approved safety
storage cabinet listed by UL or FM, the paint color is
not an issue.  However, any fusible link,  labels, and
signage on the inside and outside of the cabinet are
not to be painted over or concealed.


Loren R. Johnson - CFPS, CET
Fire Protection Systems Consultant
Marquette Heights, IL
--- Todd Williams - work <[EMAIL PROTECTED]> wrote:

This may be a stupid question, but is there any
reason a FL cabinet
can't be painted whatever color you want?


At 11:35 AM 4/13/2007, you wrote:
>Cabinets of this type in various sizes are
available from "Global
>Industrial" see their web site
www.globalindustrial.com
>They have from 80 liter to 400 liter capacities,
self closing doors,
>and meet NFPA std.
>
>Thom McMahon
>Firetech, Inc.
>2560 Copper Ridge Dr
>Steamboat Springs, CO 80488-2136
>Tel: 970-879-7952
>Fax: 970-879-7926
>----- Original Message ----- From: "Kurt Kingston"
<[EMAIL PROTECTED]>
>To: <[EMAIL PROTECTED]>
>Sent: Friday, April 13, 2007 9:11 AM
>Subject: RE: Flammable liquid storage cabinets in
retail stores
>
>
>Michael,
>One solution we used to keep everybody happy
(happier) was to use some
>commercial Velcro in strips on the cabinet face and
also on the backs of
>empty product containers. The products are
displayed on the exterior
>that way.
>I think I was watching a news story of a human dart
contest in NZ with
>guys throwing their Velcro jumpsuit equipped mates
onto the walls in a
>bar, so you must have ready access to the Velcro
product down there?
>Kurt Kingston
>Commercial Fire Protection Inc.
>
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED]
On Behalf Of Michael
>James
>Sent: Thursday, April 12, 2007 7:37 PM
>To: [EMAIL PROTECTED]
>Subject: Flammable liquid storage cabinets in
retail stores
>
>Hello,
>
>We have a retail store that sells a limited amount
of class 1B flammable
>liquids in 4 litre plastic containers for paint
thinning and brush
>cleaning
>and the sprinkler protection schemes seem very
expensive compared to
>what is
>required for the rest of the store. The quantity
stored is around 500
>litres
>hence our AHJ has suggested that flammable liquid
storage cabinets would
>be
>an acceptable alternative.
>
>Does anyone know of a manufacturer of flammable
liquid storage cabinets
>complying with NFPA 30 that would be suitable for a
retail store i.e not
>a
>bright red or yellow steel box but possibly
something with fire rated
>glass
>fronted doors or a roller shutter closing on a
fusible link. While I
>don't
>mind the look of a bright red box the merchandising
department has other
>ideas.
>
>
>
>Thanks,
>
>Michael James
>Fire Safety Engineer
>Pacific Consultants
>Auckland
>NZ
>
>_______________________________________________
>Sprinklerforum mailing list
>[EMAIL PROTECTED]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[EMAIL PROTECTED]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[EMAIL PROTECTED]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



__________________________________________________
Do You Yahoo!?
Tired of spam?  Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to