How do you propose to drain the system?
At 05:05 PM 4/17/2007, you wrote:
I've got a outdoor amphitheatre that needs sprinkler protection. The
only option allowed to get from the controls (adjacent heated building)
to the arch on the amphitheatre is to go underground. We will be using
galvanized pipe for the dry system for the amphitheatre.
The question is what pipe should I spec for the dry underground? Can
(should) I use galvanized? Do you sleeve it? Any other suggestions?
Thanks,
Reed Roisum
Fire Protection Technician
Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com