What about stainless steel? Along the lines of the "In Building Riser" from
Ames? Instead of the just the transition/riser portion, use stainless all
the way.
http://www.nickelinstitute.org/index.cfm/ci_id/14414.htm

Richard Malek
[EMAIL PROTECTED]


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Mark
Sornsin
Sent: Wednesday, April 18, 2007 1:19 PM
To: [email protected]
Subject: RE: Underground Dry Pipe


FYI:

We've been given the go-ahead to locate the dry valve in a room below
the stage (and below grade).  We will pipe horizontally underground from
that room to a point near one of the glue-lam arches that support the
stage canopy (with slope back to the room). Drainage is no longer a
problem.
We're looking into the wrapping of galvanized pipe.  I know some out
there would recommend cathodic protection as well.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
701.280.8591
[EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Wednesday, April 18, 2007 10:44 AM
To: [email protected]
Subject: RE: Underground Dry Pipe

3M Scotchrap is what I have used in similar situations.  I have a cut
sheet
for it if anyone is interested.  Let me know and I will email it out to
you.
As far as drainage, Eric already mentioned it, a big ugly pit.

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- work
Sent: Wednesday, April 18, 2007 7:40 AM
To: [email protected]
Subject: Re: Underground Dry Pipe

If I recall, on one project with a sidewalk siamese where we couldn't
use regular DI for the underground portion, we used schedule 40
galvanized with some kind of wrap and primer over. This might work in
this situation. The drainage is still a problem.



--
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 269.5.0/763 - Release Date: 4/16/2007
5:53 PM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to