Used for storage I'd protect it just like a garage. Use anti-freeze in at
least that portion of the system, with and anti-freeze loop to the two
heads, or even one head if you have enough pressure, and change the riser
backflow to an RPZ type.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Greg McGahan" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, April 19, 2007 7:36 AM
Subject: Storage Space13D/R
We have a 13d building on pilings with a 20x12 storage area underneath
that
is enclosed by lattice.
Do you think the lattice is substantial enough of an enclosure to require
additional protection?
As always in North Florida, the big deal is not a couple of sprinklers,
but
rather how to freeze protect 2 sprinklers and piping without a large
expense
to the owner.
Dry Sprinklers may not be feasible due to the fact that the piping feeding
them would be only protected with plywood and vinyl and I am uncertain
that
there is sufficient radiant heat to protect it from freezing.
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)