While it's possible for someone to classify the building as F-2 per the
IBC (Metal Products-fabrication and assembly) I'd be cautious because it
could easily be an F-1 Occupancy which would make it Ord 2.    Often
architects and other non fire protection enlightened individuals look at
the big product and determine it to be non-hazardous.  Don't forget
about cutting oils, hydraulic fluids, solvents for cleaning machines and
parts, metal dust from machining and deburring processes, conveying
ducts from equipment just to name a few forgotten hazards.  Where are
they storing these fluids, how much is also an issue since it's a
non-sprinkled building.  Their quantities are very limited.  Wonder if
they know that?  Plus with a 300K sq. ft. building, how are they or are
they meeting egress requirements with it being non-sprinkled?   Is there
rack storage for finished products or for incoming parts or materials or
other supplies?  Rated fire separations between office and mfg
occupancies?  I'd have a bunch of questions I'd be asking someone,
otherwise this whole project could go sour real fast.  Also for a
building that size, do they have an insurance underwriter on board?
That could definitely send things in a different direction.

Just a few things to ponder,


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Monday, April 23, 2007 2:48 PM
To: [email protected]
Subject: Water supply NFPA 14 Standpipe & Hose System

I'm designing a class 3 standpipe system for a single storey 300,000
sq.ft.
metal fabrication plant. No city water, so needs a water storage pond.

I'm trying to figure out the required storage volume. NFPA requires 500
gpm from the most remote standpipe and 500 gpm from each additional
stand pipe (for floor area exceeding 80,000 sq.ft.) with total not
exceeding 1250 gpm, for a duration of 30 minutes. My opinion is that
NFPA 14 mostly covers multi-storey buildings. When it's single storey,
should I take each hose connection as a standpipe and flow 250 gpm per
connection, up to maximum 1250 gpm? It is probably the safest, as it
would be the most conservative.
Has anyone come across this situation?

The other question is regarding hose allowance for fire department. (The
building code water supply requirement does not apply in my area, if the
building has either a sprinkler or standpipe system.) NFPA 14 requires a
standpipe system to be designed for the system demand and fire
department connections. It says to consult the AHJ for water supply from
fire department pumper. Would it be system demand OR demand for fire
department pumper (the larger value and not both simultaneously)? Or
should a hose allowance be used same as for a sprinkler system? If so,
for what duration?

Another question (while I'm at it), NFPA 14 requires lateral piping to 2
1/2" hose connections to be protected if the building is not
sprinklered. Up to now I've never seen piping in a single storey
building in fire rated enclosures. Is it required?

Tony      

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to