Scott - verify the size of main in the street.  NFPA 13D doesn't require a
traditional flow test (only a static pressure), but it's based on the
assumption the public water main is 4" minimum.

If the main is indeed less than 4", a traditional flow test is justified.
Even at the low total flow of 2 residential sprinklers, the pressure drop
(residual pressure) in the 1 1/2" main can be significant.  Now how to
conduct a flow test on a 1 1/2" line is a whole different can of worms.

Ed Kramer
Littleton, CO.



>> Do you recommend flow tests for residential systems?
>> I want one, but most people are telling me, the 1.5 inch pipe out in
>> the street with 50 psig is enough.  (1.5 inch?????)
>>
>> Does not seem like enough information to me.  Don't have a level of
>> comfort with it.  Have 2 stories above grade and want to use extended
>> coverage heads.