Hmmmm, a "special one of a kind system",   was this in the 1985 edition
of NFPA 13?  The oldest I've got at the office is '89, my '87 is at the
house (that way the ME's here won't use it anymore, LOL)  But this type
system was in the '89.  Often on these type of systems it may take years
before this type of deterioration becomes evident.  But the thing is,
for circulating hvac systems we don't run hot or chilled water through
black steel piping without some sort of chemical treatment.  It sounds
like the condition of this system is from lack of proper treatment and
maintenance along with some installation/design errors.  But the
arm-overs are not the big issue since in a lot of if not most systems
being served by a treated municipal water supply, you don't need to use
arm-overs, might still be a good idea but arm-overs are generally
reserved for raw water systems.  Were there adequate flushing
connections, were they used if present, who inspected the systems and to
what level of detail is what I'd be asking.  

Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Michael
M. Fitz
Sent: Wednesday, May 02, 2007 3:28 PM
To: [email protected]
Subject: RE: So what's this return bend thing?

I can't respond to the number of high-rise buildings that aren't
sprinklered in Seattle........Rich?

According to the information I was given, there were two buildings
designed for a local developer that used a combined HVAC and sprinkler
system.  Unfortunately, pendant sprinklers were used in some locations
along with the connections from the bottom of the pipe.  Guess where the
debris ends up?

I was shown two heads, both of which were not plugged or obstructed in
any way that had me concerned.  I was led to believe that there were a
substantial number of heads that were totally plugged and that is the
reason for the major "maintenance".

The "maintenance" procedures I have seen in photographs or was told
about involved tapping the top of the pipe where there was access or
from the side of the main or branch.

As an engineer, I was impressed with the condition of the pipes as old
as they were.  I suspect this is because there was water treatment for
the HVAC usage.

Michael


At 11:52 AM 5/2/2007, you wrote:
>I would be interested to know how many high-rise buildings there are in

>the town - that don't have sprinklers at all.  Hmmmmmm?
>
>Terri Simmons Leyton
>PROTECTION DESIGN & CONSULTING
>Ph:      858-751-2930
>Fax:    858-751-2933
>Cell:  619-871-8450
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Rod 
>DiBona
>Sent: Wednesday, May 02, 2007 11:49 AM
>To: [email protected]
>Subject: RE: So what's this return bend thing?
>
>The craftsman was concerned with the integrity of the sprinkler system 
>because the buliding had been mentioned as a prime terrorist target.
>That's interesting.
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Jamie 
>Seidl
>Sent: Wednesday, May 02, 2007 12:11 PM
>To: [email protected]
>Subject: So what's this return bend thing?

Michael M. Fitz, P.E., C.F.I.
MDE Inc.
700 South Industrial Way
Seattle, WA  98108
Main 206-622-2007
Direct 206-957-2140
Fax 206-622-2248
Home Office 360-427-2751
Cell 206-321-1804
www.mde.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to