Following a stint of leaking CPVC systems (mostly in PA it seemed)
which were using antifeeze, Noveon (BF Goodrich still sounds right)
studied it. Besides having BFP's with no expansion chambers, they
specified the needed taping amount (all tapes are not the same
thickness) and more importantly said don't tape and dope. Just say no.
Roland
On May 4, 2007, at 7:01 AM, Greg McGahan wrote:
I am just curious as to how many companies are using ONLY teflon
tape now.
Anybody having succes with plastic head adaptors (brass insert) not
leaking
when using only teflon?
Thanks,
Greg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)