They claim it is. Their data does not specifically say branch lines, but
"fire suppression piping". 

We had a situation where the engineer spec'd freeze protection and that was
the ONLY way to do it. I won't bore you with details but trust me, nothing
else would work.

The local AHJ approved the use and we installed it. In our case the Freeze
protection is predominantly unnecessary so I am not really worried about it.
We did it to satisfy the engineer and avoid 20 deluge systems on a
residential building (which was the other option). 

Remember where we live. We literally only need freeze protection once every
several years if the pipe is installed concealed behind almost anything and
the wind is not blowing directly over it. The last time we had a freeze
where sprinkler systems were affected in significant quantities was
approximately 10 years ago. And before that it was probably 10-12 years. 

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Monday, May 07, 2007 11:55 AM
To: [email protected]
Subject: Re: Electric Heat Tracing - Background

The use of heat tape went through a major change for the 07 edition,   
Now there is criteria in the body that says heat tape shall be  
supervised and if used for branch lines, it shall be specially listed  
for branch lines.  I haven't looked lately but the last time I looked  
there were no such listed products.

Greg - was the Chromalox listed for BL's?

As a side note, it still says SMALL UNHEATED AREAS can use antifreeze  
or heat tracing.  I would say heat trace is intended to be used only  
for portions of a systems but considering there are antifreeze  
systems in freezers that are 1,000+ gallon systems, I guess small is  
relative.


Roland

On May 5, 2007, at 5:58 PM, Dave Phelan wrote:

> Hello again all,
>
> Im looking for the wisdom and experiences off the list for projects  
> that
> used electric heat tape for freeze protection.  I currently have a  
> 13R-2002
> (metallic piped) project where the owner is looking to use the  
> Raychem XL
> Self Regulating heat trace for supplemental freeze protection.  The  
> piping
> will be insulated as per the code but they want a belt and suspenders.
>
> Im looking for the code background as to why the appendix specifically
> prohibits branchlines - rather forceful language I thought to be in  
> the
> appendix and not the code itself but oh well.  The project natually is
> looking to heat trace the crossmains and branches up to the drops  
> for the
> concealed pendants in the living space, hence my concern.
>
> The product is reportedly listed UL for Fire Protection piping but  
> I am
> still awaiting all of that submission, in the mean time I need to  
> educate
> myself as to the why's and why not's in the code and branchline  
> prohibition.
>
> Thank you once again.
>
> Dave P.
> An AHJ in New Jersey
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to