Hello Paul, Got my coffee and construction calculator working now and it looks like 113.5556 cubic feet
Tuesday, May 15, 2007, 8:44:52 AM, you wrote: > Check your math, but first convert 14" to 1.167'. > Paul J. Pinigis, P.E. > Chief Life Safety Engineer > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Coastal > Sent: Tuesday, May 15, 2007 8:40 AM > To: [email protected] > Subject: Pockets or just plain Obstructions > Hello sprinklerforum, > I have a 2 story butler building where the center area of the 2nd > floor is supported by 14" deep steel beams exposed to the floor below. > The space between the beams are 24'-4" long x 4' Wide and the beams are > 14" deep supported at each end by a 16" deep beam. IF I did my math > right that figures to 1362.666 cubic feet in each space. Heads down the > length of each space? Sidewall head at each end in each space? This is > a light hazard building. The space under these beams will be a game room > for a Youth Christian Center. I am open to suggestions to protect this > area AND keep the pool cues away from the sprinkler heads...... -- Best regards, Charles mailto:[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)