I design with concealed sprinklers in such pockets. If the contractor feels it is not required, I let him negotiate with the AHJ.
NFPA always had a section that permits deletion of heads in a concealed space above an isolated small room not exceeding 55 sq.ft. (NFPA 13, 2002, 8.14.1.2.9) I have never come across a situation where it could be applied. But many times the folding partition pockets and similar linen closets. Could it be this section would apply? Just thinking. Tony -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - work Sent: May 28, 2007 6:34 AM To: [email protected] Subject: folding door alcove A question came up on a hotel with a meeting room that could be divided in two by a folding partition. The partition folds into a space roughly the size of a closet. The ceiling of this space is mostly track that partition runs on. Does this space need to be sprinklered? If so, does anyone have any good ideas how to do it? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
