Roland, I agree the QR sprinkler reduction is applied to whatever size the
initial design area is determined to be.  We apparently disagree on the
minimum size of the initial design area.

My position is that when utilizing the Density/Area Method, section
11.2.3.2.1.2 and the curves of Fig 11.2.3.1.5 dictate an initial DA of
nothing less than 1500 sf.  The DA increases and reductions are then
applied.  In Rich's original scenario, this would result in a revised DA of
900 sf and a density (assuming light hazard) of .10 (per section 11.2.3.1.8
(1)).  If Rich's building had been 800 sf, then the DA would be the entire
800 sf. 

So let's ignore section 11.2.3.2.1.2.  As a designer/contractor wanting to
retire early, why wouldn't I select a DA of 200 sf and then reduce it by
40% to 120 sf (regardless of whether it's a 1,000 sf building or 60,000
sf)?  What section in the standard differentiates between buildings larger
than 1500 sf and those smaller than 1500 sf?

Ed Kramer
Littleton, CO

>
>Well allow me to disagree and suggest you step out of the quicksand.
>There is plenty of justification when the total building size is only
>1,000 sf. 11.2.3.1.8 (1) explicitly addresses areas less than 1500
>sf.  Also look at the wording in section 14.4.4.4.2 (02 edition)
>regarding closets where it says "the minimum allowable area of Fig
>11.2.3.1.5".  I don't see anything like that in the QR reduction
>section.  There is nothing that says anything about minimum allowed
>size is 900 sf either.  Thus we are back to applying the reduction to
>what ever the initial size is then ensuring we still have at least 5
>sprinklers.
>
>Don't confuse this with bigger buildings and simply wanting to have a
>smaller remote area.
>
>Roland