Travis, My read is that even if your not in a seismic zone you need to follow all the other hanging and bracing rules. Since it's laid on the truss there is no HANGING but it still needs to comply with the 40'/80' BRACING rules. Then again I'm about to be shaken into the sea at any time so I brace seismically without as a matter of habit. As to your actual question I'd say on my liberal side that if the hangers aren't being used for anything except alignment then it doesn't matter, my conservative side says that since they look like a duck I'd expect them to act like a duck and so since they don't quack I'd remove them to avoid confusion, and finally my wacko AHJ side says that since they have no standard (standard as in NFPA 13) derived function then they're not part of the system and so they must be removed as a non-system component attached to the system.
On 7/31/07, Travis Mack <[EMAIL PROTECTED]> wrote: > In a 13R application, the sprinkler contractor installed the sch 40 steel > piping so it is laying on the bottom chord of the trusses. He then > installed 2 hole straps (listed for CPVC only) in order to keep the pipe > from moving to aid installation. Do the straps have to be listed for fire > protection use? I was under the impression that since the piping is laying > on top of the bottom chord, it is not being "hung." Therefore, the straps > are merely for convenience. What do y'all think? Bracing or restraint is > not required by the AHJ in this area. > > Travis > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)