Sorry, I should have mentioned the 2007 version of NFPA 24. And, by the way, 
yes I know how to use the spell checker, I just forgot.
Mark at Aero

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Phelps,
Mark
Sent: Tuesday, July 31, 2007 5:25 PM
To: [email protected]
Subject: Erratta in NFPA 24


Has anyone acknowledged the error in the formula in paragraph C.4.7.3(having 
ommited the 29.84 value)?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Travis
Mack
Sent: Tuesday, July 31, 2007 10:00 AM
To: [email protected]
Subject: Pipe supported from truss


In a 13R application, the sprinkler contractor installed the sch 40 steel
piping so it is laying on the bottom chord of the trusses.  He then
installed 2 hole straps (listed for CPVC only) in order to keep the pipe
from moving to aid installation.  Do the straps have to be listed for fire
protection use?  I was under the impression that since the piping is laying
on top of the bottom chord, it is not being "hung."  Therefore, the straps
are merely for convenience.  What do y'all think?  Bracing or restraint is
not required by the AHJ in this area.  

Travis 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to