And once again bretheren we shall heap praise upon the existence of
the list. All hail the list. Having a little knowledge and admitting
to only having half a clue got me so much help from the AHJ--an
acceptable alternative in leiu of the SUSE label. I draw your
attention to the other thread. And I didn't have to resort to what the
Turks call Baksheesh as, with tongue in cheek, suggested by the last
poster. Thanks again folks.

On 8/1/07, Jim Davidson <[EMAIL PROTECTED]> wrote:
> The NEC - 230.66 Marking "Service Equipment rated at 600 Volts or less
> shall be marked to identify its as being Suitable for Use as Service
> Equipment (SUSE)."  This mark is supplied by the controller manufacturer
> when specified and does not add any cost to the controlled. It is a
> label placed inside of the controller housing by the manufacturer.
>
> On all PO I require that all controllers be SUSE label.
>
>
>
>
> Jim Davidson
>
> Davidson Associates
> 302-378-7600
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of John
> Drucker
> Sent: Wednesday, August 01, 2007 5:01 PM
> To: [email protected]
> Subject: RE: SUSE
>
>
> The code reference can be found in the 2005 NEC - 230.66 Marking -
> "Service
> Equipment rated at 600 Volts or less shall be marked to identify its as
> being Suitable for Use as Service Equipment (SUSE).  The listing should
> include this designation.  Since a FP Controller can be connected
> directly
> to the utility service entrance it must be listed as SUSE in order to be
> used in this application.
>
> John Drucker
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of
> [EMAIL PROTECTED]
> Sent: Wednesday, August 01, 2007 4:31 PM
> To: [email protected]
> Subject: RE: SUSE
>
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Ron
> > Greenman
> > Sent: Wednesday, August 01, 2007 3:14 PM
> > To: [email protected]
> > Subject: SUSE
> >
> > Has anyone heard of an approval agency called SUSE? according to one
> of
> > our AFSA members there's an electrical inspector hereabouts requiring
> > fire pumps to be SUSE approved. I'm trying to help him out but don't
> > know what this even is.
> >
> > --
> > Ron Greenman
> > at home....
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to