Brian:

That depends on the shape of the system you're bracing and the on-center
spacing of EQB's that you've selected.   If you go to the full 40'
allowed for lateral bracing, then you have to include all of the branch
and main piping that falls into the most demanding 40' "patch" of main
being braced.   If it's a grid, then you go half-way out the branches
and include the tailbacks in the same lineal patch (the other half of
the lines are presumed to influence the opposite main).   Look at the
figures in the annex of whichever version of the standard you're using,
as the diagrams are helpful if you tilt the page just so and close one
eye ...

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Monday, August 20, 2007 8:57 AM
To: [email protected]
Subject: RE: Seismic ZOI

I ain't seeing it, isn't there somewhere that explains how to determine
where (how big) the Zone of Influence is? 


 
 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of G. Tim
Stone
Sent: Monday, August 20, 2007 10:42 AM
To: [email protected]
Subject: RE: Seismic ZOI

Brian,
Refer to 2002 ed NFPA 13, Chapt. A9.3.5.6, (3,a,b).
This should help.

G. Tim Stone


NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

117 Old Stage Rd. - Essex Jct., VT. 05452
TEL: (802) 434-2968          Fax: (802) 434-4343
                [EMAIL PROTECTED]

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-

> [EMAIL PROTECTED] On Behalf Of Brian Harris
> Sent: Monday, August 20, 2007 9:08 AM
> To: [email protected]
> Subject: Seismic ZOI
> 
> I'm having a brain cramp this morning so your help would be greatly 
> appreciated. I haven't done seismic in a while and I can't remember 
> the criteria to determine the Zone Of Influence, help a brother
out......
> 
> 
> 
> 
> 
> 
> 
> 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to