Hi all,
  For designing a total flooding high pressure carbon dioxide system in a 3,500 
cubic feet computer room with electrical equipment and cable runs, I have 
specified my room as "Dry electrical hazard" with flooding factor of 0.083 
lb/cubic.feet and 50% design concentration according to NFPA-12.
  My questions are as below:
  1)- Is a computer room fire a deep seated fire?
  2)- NFPA 12 states that "For deep-seated fires, the design concentration 
shall be achieved within 7 minutes, but the rate shall be not less than that 
required to develop a concentration of 30 percent in 2 minutes." Is it a 
problem if the total discharge time would be only 1 minute for this case?
  Many thanks for your help in advance.
  Reza

       
---------------------------------