Reza:

I would not recommend a CO2 system as it is potentially too dangerous.  I
would consider a clean agent sytem per NFPA 2001.

Hopefully, this is only a back-up to a wet pipe system, which is still my
favorite.

Regards,

James L.(Jim) Roberts, PE, SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)



                                                                                
                                                        
                       Reza Esmaeili                                            
                                                        
                       <[EMAIL PROTECTED]>                                      
                                                
                       Sent by:                                                 
                                                     To 
                       [EMAIL PROTECTED]         
[email protected]                                            
                       prinkler.org                                             
                                                     cc 
                       08/23/2007 10:18 AM                                      
                                                        
                       Please respond to                                        
                                                Subject 
                       sprinklerforum                       Carbon Dioxide 
System Discharge Time                                        
                                                                                
                                                        
                                                                                
                                                        
                                                                                
                                                        
                                                                                
                                                        
                                                                                
                                                        
                                                                                
                                                        
                                                                                
                                                        




Hi all,
  For designing a total flooding high pressure carbon dioxide system in a
3,500 cubic feet computer room with electrical equipment and cable runs, I
have specified my room as "Dry electrical hazard" with flooding factor of
0.083 lb/cubic.feet and 50% design concentration according to NFPA-12.
  My questions are as below:
  1)- Is a computer room fire a deep seated fire?
  2)- NFPA 12 states that "For deep-seated fires, the design concentration
shall be achieved within 7 minutes, but the rate shall be not less than
that required to develop a concentration of 30 percent in 2 minutes." Is it
a problem if the total discharge time would be only 1 minute for this case?
  Many thanks for your help in advance.
  Reza


---------------------------------
Pinpoint customers who are looking for what you sell.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to