Jay, section 8.6.5.1.2 says to comply with ONE of subsections that follow
it - you don't need to comply with more than one.  So if you can make
subsection (1) work for you (Table 8.6.5.1.2), you're good to go.

Ed Kramer
Littleton, CO


>I have a school with classrooms that have a ceiling of 8'.  there is a
>soffit along one wall that is 10" lower than the ceiling and 36" wide.  I
>am
>drawing a blank as to whether I need sprinklers in the soffit.
>8.6.4.1.1.3
>says that if the difference in heights in the ceiling is less than 36", I
>can consider it a flat ceiling.  8.6.5.1.2 (3) limits the soffit to 30" in
>width.  I can comply with table 8.6.5.1.2 and be less than 7'6 away from
>the
>wall.  So can I eliminate sprinklers in the soffits?
>
>Joseph C. Stough SET, CFPS
>Tilley Fire Equipment Co.
>Tel. 215-345-8066 X22
>Fax: 215-345-9357
>[EMAIL PROTECTED]