Besides the Erico and Sammy products, Tolco has a universal swivel the you can 
install on most  rod-type clamps and anchors that allows the load to hang plumb 
even if the attachment is sloped. 


Steve Leyton

Away from the office - sent from my BlackBerry

-----Original Message-----
From: "Cliff Whitfield" <[EMAIL PROTECTED]>

Date: Thu, 27 Sep 2007 10:54:15 
To:<[email protected]>
Subject: RE: Pipe clamps on Z purlins


I have dealt with one building manufacturer that allows (even recommends) a
type of 'C' clamp that is offset a little and fits over the lip of the
purlin and fastens in the middle of the bottom lip.  The clamp is made by
Erico but I can't remember the model number.  I still prefer to hang to the
middle (side) of the Z like Matt mentioned.  It is by far the strongest
point of connection. 

Cliff Whitfield
Fire Design, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew J.
Willis
Sent: Thursday, September 27, 2007 10:45 AM
To: [email protected]
Subject: RE: Pipe clamps on Z purlins

Its' not the code that I am aware of..,  but the structural people or the
Manf. of purlins. In the side is the way to go. Be aware if the slope is >1
or so, they have a new swivel one..
R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Brian Harris
----- >Sent: Thursday, September 27, 2007 10:40 AM
----- >To: [email protected]
----- >Subject: Pipe clamps on Z purlins
----- >
----- >What is the preferred method of hanging sprinkler pipe 
----- >from a Z-purlin?
----- >Sammy sidewinder I would assume. Someone recently asked 
----- >about using a standard top beam clamp on a Z-purlin, I 
----- >know that's not the way we do it but where in the code 
----- >does it say you can't?
----- > 
----- >Thanks,
----- >Brian
----- > 
----- >
----- > 
----- >
----- > 
----- >
----- > 
----- >
----- > 
----- >

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to