I have never understood this requirement. Most of the time if we have to
flow from the top we achieve the 500 gpm through one valve.
We have also used the valve on the landing below due to the absence of 2 at
the top.

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Monday, October 01, 2007 11:11 AM
To: [email protected]
Subject: RE: Hose connection for testing

The other question is whether it is of any practical use? Most buidings I
come across (maybe 95%) have sloped roofs. If the additional hose valve is
provided, is it really used for testing? Or is it provided, just 'cos the
code requires it?

I would also like to hear from those that don't provide the additional hose
connection for testing.

Tony 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: October 1, 2007 8:03 AM
To: [email protected]
Subject: RE: Hose connection for testing

We have been providing 2 hose valves on the hydraulically most remote
landing when there is access to the roof top.  If there is no access and the
pitch is less than 4/12 then we have been providing a control valve inside
the stair well with some galv pipe going through the roof to the
2 hose valves.   
Dewayne   

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Monday, October 01, 2007 1:03 AM
To: [email protected]
Subject: Hose connection for testing

 
NFPA 14 requires "an additional 2 1/2" hose connection" at the highest
landing (if stairs go up to the roof) or at the roof, at the hydraulically
most remote standpipe riser to facilitate testing of the system. I've never
seen an additional hose connection being provided.
I've been told by contractors that the hose connection at the highest floor
level can be used for this purpose, which would be a difficult task as most
buildings don't have access to the roof.

What is the normal practice out there?

Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to