In an emergency can the fire department get the pumps turned on? In one
small town the I set up the water flow switch to turn on a booster pump 1/2
mile away.

Art

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Monday, October 01, 2007 4:30 PM
To: [email protected]
Subject: water supply fluctuation

I just ran into a situation that makes me a little nervous about 
water department flow tests. I have been asked to straighten out a 
mess on a system in a 7 story condo (multiple issues). A designer who 
was asked to verify some hydraulics got a flow test from the 
municipality which was about 23 pounds higher than the design test, 
which was done several years ago. At that time, she was told this was 
due to improvements in the public system. They had been doing a lot 
of work on the system, so it was believable. System pressure gauges 
were with a reasonable number of the static pressure. When I got on 
board, I also checked with the water department and was told the same 
thing. Recently, a contractor working on the system noticed the the 
pressures reading lower. Upon further investigation, including 
pressure recorders on hydrants, it was found that the pressures 
varied 30 psi over a 3 day period. The water department was not aware 
of the range of fluctuation until they did this test. Their 
explanation was various pumps kicking in to fill tanks, including for 
the town's largest water user. Now we are going back and 
re-calculating the systems with a much lower static pressure. Has 
anybody run into this type of thing? Is there a good way to detect 
it? I consider myself fairly savvy and sniffing out problems, but 
this caught me off guard. How can a water department not know this 
type of thing is going on. This is a small city in CT.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to