The water departments don't know about it because few if anyone would
call and report low water pressure in their shower, they just deal with
it.  So if no one bothers to report a problem, there's no way they'll
know.  

Had a similar situation a few years back.  Could not get a dry system to
pass the trip test for the AHJ, we verified and reverified information
given us, triple checked the installation and finally had another flow
test performed and the numbers were all different.  Had several tests
done and numbers varied each time.  Finally the water department came to
a conclusion that based on various new users in their system, the flow
data would fluctuate with no apparent consistency.  But until we raised
the flag, they had no idea that their system fluctuated so widely during
any given day.  


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- FPDC
Sent: Monday, October 01, 2007 4:30 PM
To: [email protected]
Subject: water supply fluctuation

I just ran into a situation that makes me a little nervous about water
department flow tests. I have been asked to straighten out a mess on a
system in a 7 story condo (multiple issues). A designer who was asked to
verify some hydraulics got a flow test from the municipality which was
about 23 pounds higher than the design test, which was done several
years ago. At that time, she was told this was due to improvements in
the public system. They had been doing a lot of work on the system, so
it was believable. System pressure gauges were with a reasonable number
of the static pressure. When I got on board, I also checked with the
water department and was told the same thing. Recently, a contractor
working on the system noticed the the pressures reading lower. Upon
further investigation, including pressure recorders on hydrants, it was
found that the pressures varied 30 psi over a 3 day period. The water
department was not aware of the range of fluctuation until they did this
test. Their explanation was various pumps kicking in to fill tanks,
including for the town's largest water user. Now we are going back and
re-calculating the systems with a much lower static pressure. Has
anybody run into this type of thing? Is there a good way to detect it? I
consider myself fairly savvy and sniffing out problems, but this caught
me off guard. How can a water department not know this type of thing is
going on. This is a small city in CT.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to