Hello Dave,

Ames makes a SS lead in for sprinkler risers that comes from outside the slab 
and turns up to sit the Riser on. Has all kinds of good listings and ratings 
for contact with various sub-surface items.  
http://www.amesfirewater.com/products/_productsFull.asp?catId=154&parCat=154&pid=363&ref=2

Saturday, October 6, 2007, 4:34:04 PM, you wrote:

> Greetings again all,

> I am in the process of reviewing plans for the secondary water source to a
> high-rise residential building where they are taking water from the pool on
> the parking garage roof and piping to the grade level fire pump room.  All
> indications are that there is enough head pressure to overcome friction and
> fitting loss even at the max. 1500 GPM flow to make this a do-able solution.

> They have selected to use 8" sch 10 or 40 stainless steel piping for the
> approx. 215 foot distance between the pool drain and pump room, which
> happens to be exposed overhead - aboveground piping through two levels of an
> open parking garage.  They are indicating that this is the best material for
> the application since chlorinated pool water will sit in the pipe
> indefinately awaiting a seismic event.  Here's my dilemma(s):

> a.      I have no previous experience in reviewing or inspection systems with
> stainless piping.  I also dont think it is listed as an approved AG material
> in NFPA 13 or 24 of any edition. (99,02,07).  Does anyone on the list know
> of a type / brand of fire protection listed stainless steel pipe?

> b.      Is this really the best material for the application?  I mean sure I 
> hear
> the word on the street is stainless is very resistant to ACQ lumber and for
> boat railings .... does that also mean its right for pools supplying
> sprinkler systems?  I was also wondering since this is almost a near vacuum
> application, versus a pressure application, would stainless be as resilent
> and durable with the atmosphere pushing in on it from the outside and large
> volume flows and a fire pump pulling in on it from the inside.

> c.      I understand from the plumbing consultant who is working on the plans
> (YIKES!!) that Victaulic makes a grooved coupling and fittings that are
> stainless ... but could not tell me if they are also listed for FP use since
> I have seismic design and differential movement requirements in the project
> and somewhere along that piping I will need 'flexible' couplings.

> Much appreciate the assistance once again.

> Dave P.
> An AHJ in New Jersey


> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)



-- 
Best regards,
Charles Thurston 
 Coastal                            mailto:[EMAIL PROTECTED]