Reduce the possibility of future sprinkler pipe obstructions. Increased corrosion growth evident in dry pipe sprinkler systems, especially with smaller diameter pipe.
Rick E. Green, District Manager East Coast Fire Protection, Inc. 1113 Cavalier Boulevard Chesapeake, Virginia 23323 757/485-7486(p), 757/485-8730(fax), 757/328-0131(cell) [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight Sent: Thursday, October 18, 2007 5:01 PM To: [email protected] Subject: RE: 3/4" Steel Pipe on Dry Pipe System Rick, There are no NFPA 13 criteria for changing 3/4" pipe in the manner that you have described. What would the benefit be to your customer to change the 3/4" to 1"? Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Rick Green Sent: Thursday, October 18, 2007 2:47 PM To: [email protected] Subject: 3/4" Steel Pipe on Dry Pipe System East Coast recently completed inspection of a dry pipe sprinkler system. During trip test unable to trip the dry pipe system because of foreign material causing pipe blockage. Initially pipe blockage was notice in the inspectors test pipe. After a thorough inspection, majority of the pipe including mains, branch lines showed signs of foreign material in the pipe. We have proposed to owner to flush sprinkler system and also replace ¾" branch line pipe. Is their a standard reference that requires removal of 3/4" sprinkler pipe with larger diameter pipe (1") when the sprinkler pipe is flushed? Rick E. Green, District Manager East Coast Fire Protection, Inc. 1113 Cavalier Boulevard Chesapeake, Virginia 23323 757/485-7486(p), 757/485-8730(fax), 757/328-0131(cell) [EMAIL PROTECTED]<mailto:[EMAIL PROTECTED]> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.488 / Virus Database: 269.15.0/1077 - Release Date: 10/18/2007 9:54 AM No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.488 / Virus Database: 269.15.0/1077 - Release Date: 10/18/2007 9:54 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)