Mike, Please;

[EMAIL PROTECTED]
 
John
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of MIKE HENKE
Sent: Friday, October 19, 2007 5:10 PM
To: [email protected]
Subject: RE: Fire Pump Test Header Valve Supervision

Make sure about it monitoring the valve in the closed position. Chances are
you will have to almost completely open the valve before the switches will
activate.
Typically the switches are set to activate within the first 2 revolutions of
the handwheel or 1/5 of the valve travel from the fully open position.
So if you wire it to monitor the valve closed, most likely you will have to
open it to within 2 revolutions of fully open or 4/5 open before the
switches will trip. Confirm this with Vic before proceeding. They may have
special modifications for this situation.
We have handled this in the past by mounting a bracket to the outside of the
valve body and using the indicating flag to operate the standard Potter
butterfly tamper switch. I can send a drawing if necessary.

Regards,
mike

>>> "Joe Burtell" <[EMAIL PROTECTED]> 10/19/2007 12:07 PM >>>
Look at the Vic 705W Butterfly valve. I just checked the datasheet. It will
monitor in the fully open or closed position.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED] 
www.burtellfire.com 


-----Original Message-----
From: [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Wisneski
Sent: Friday, October 19, 2007 11:01 AM
To: [email protected] 
Subject: RE: Fire Pump Test Header Valve Supervision

John,

I went through the same exercise last month. The only luck I had was with
Ferguson Fire & Fab out of Tucker, GA. They have a company that will alter a
butterfly tamper to work correctly with a fire pump test header. Contact Jim
Sutton.

Mike Wisneski

-----Original Message-----
From: [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Friday, October 19, 2007 11:13 AM
To: [email protected] 
Subject: Fire Pump Test Header Valve Supervision


Does anyone have product reference for a tamper switch and or tamper
switch/valve assembly configured for use on a fire pump test header
aside from pull type (PTS) cable devices ?.

Thanks

John Drucker
_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 

To Unsubscribe, send an email to:[EMAIL PROTECTED] 
(Put the word unsubscribe in the subject field)


-- 
No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.1/1079 - Release Date: 10/19/2007
5:10 AM


_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 

To Unsubscribe, send an email to:[EMAIL PROTECTED] 
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 

To Unsubscribe, send an email to:[EMAIL PROTECTED] 
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to