In Section 1016.2, it specifically states (requires) smoke and heat vents along with an automatic sprinkler system in accord with blah blah blah in order to increase the egress dimension. You are correct that Table 2306.2 provides a note that allows the omission of smoke and heat vents when ESFR sprinklers are used, however you are sort of dealing with apples and oranges. Chapter 23 is High Piled Storage. Chapter 10 is Means of Egress. Chapter 23 may allow the omission of vents, but since the objective is to increase the egress dimension (albeit in a HPS facility) then Section 1016.2 trumps Chapter 10 and venting is required vents regardless of the type of fire sprinkler system is provided as long as an approved system is in fact provided.
Note also Section 102.9 Conflicting provisions. This may be an example of that. Section 1016.2 appears to be more specific than other sections that were referenced. My opinion as an AHJ. I agree with the double dipping statement with ESFR's. Steve Smith Colorado Springs FD -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, October 30, 2007 10:15 AM To: [email protected] Subject: 2006 IFC - Smoke and Heat Vents In a high piled storage building may the 400 ft. egress dimension be used "without" vents if the building is equipped with ESFR sprinklers? 910.1 Exception 2: smoke and heat vents shall not be required in areas of buildings using ESFR sprinklers. Section 1016.2: allows an increase in egress dimension to 400 ft. for a building with sprinklers and vents. Table 2306.2 note j: vents are not required when ESFR sprinklers are installed. Ron Fletcher Aero Automatic Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)