In Section 1016.2, it specifically states (requires) smoke and heat
vents along with an automatic sprinkler system in accord with blah blah
blah in order to increase the egress dimension. You are correct that
Table 2306.2 provides a note that allows the omission of smoke and heat
vents when ESFR sprinklers are used, however you are sort of dealing
with apples and oranges. Chapter 23 is High Piled Storage. Chapter 10 is
Means of Egress. Chapter 23 may allow the omission of vents, but since
the objective is to increase the egress dimension (albeit in a HPS
facility) then Section 1016.2 trumps Chapter 10 and venting is required
vents regardless of the type of fire sprinkler system is provided as
long as an approved system is in fact provided.  

Note also Section 102.9 Conflicting provisions. This may be an example
of that. Section 1016.2 appears to be more specific than other sections
that were referenced. 

My opinion as an AHJ. I agree with the double dipping statement with
ESFR's.

Steve Smith
Colorado Springs FD



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, October 30, 2007 10:15 AM
To: [email protected]
Subject: 2006 IFC - Smoke and Heat Vents

In a high piled storage building may the 400 ft. egress dimension be
used "without" vents if the building is equipped with ESFR sprinklers?
 
910.1 Exception 2:  smoke and heat vents shall not be required in areas
of buildings using ESFR sprinklers.
Section 1016.2:  allows an increase in egress dimension to 400 ft. for a
building with sprinklers and vents.
Table 2306.2 note j:  vents are not required when ESFR sprinklers are
installed.
 
 
Ron Fletcher
Aero Automatic
Phoenix, AZ
 
   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to