No I meant whatever doors required if the exiting is less than the 400 allowed with vents. Your issue was related to "Section 1016.2: allows an increase in egress dimension to 400 ft. for a building with sprinklers and vents." If you don't have the vents I don't think you can use the 400'. I assume you'll need more doors to meet whatever (200'?).
Chris -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, October 30, 2007 1:51 PM To: [email protected] Subject: RE: 2006 IFC - Smoke and Heat Vents Chris, When you say doors are you referring to the 100 ft. on center man doors around the perimeter of the building? It is a spec building S-1 high piled storage 490 ft. by 1064 ft. with no interior walls. Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill Sent: Tuesday, October 30, 2007 11:22 AM To: [email protected] Subject: RE: 2006 IFC - Smoke and Heat Vents Slow down IMHO. Read the text, don't read into it. If they wanted you to take the venting and egress exceptions for ESFR they would have said it. Remember you are also dealing with exception to the base rule. I only believe you get one in your case. Either skip the vents but add doors or skip the doors and add vents. Choose the lesser of the evils. Joe will have a cow, but you could do ESFR and vents and not do the doors. Now get an FPE involved to PBD the vents and doors with ESFR to balance not full compliance with either. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [EMAIL PROTECTED] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, October 30, 2007 12:54 PM To: [email protected] Subject: RE: 2006 IFC - Smoke and Heat Vents Thanks Scot. I think the same but I had a local Architect tell me it was taking the ESFR trade off twice. Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... .... Sent: Tuesday, October 30, 2007 10:46 AM To: [email protected] Subject: 2006 IFC - Smoke and Heat Vents my opinion is yes. scot deal excelsior fire On 10/30/07, Fletcher, Ron <[EMAIL PROTECTED]> wrote: > > In a high piled storage building may the 400 ft. egress dimension be > used "without" vents if the building is equipped with ESFR sprinklers? > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)