Todd,
I know of no other sprinklers beside the Viking Coin or Tyco CC1/CC2 to
protect to CPVC pipe.  Would the FM accept if a
sign was installed on the doors stating that "no storage" is allowed
instead of sprinklers?  I think your safe with CPVC pipe in this space.
You can run pipe listed for light hazard occupancies to be installed in
ordinary hazard rooms of otherwise light hazard occupancies where the
room does not exceed 400 sq. ft.(NFPA 13 (02ed)6.3.6.2)and page 18 of
the BlazeMaster hand book.
Dewayne

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Thursday, November 08, 2007 7:27 AM
To: [email protected]
Subject: CPVC in concealed space

I am working on a school being converted to condos. This is an NFPA 13R
system using CPVC pipe in concealed spaces. The Fire Marshal has
requested that sprinklers be added in the space over the bathroom and
kitchen ceilings. The space contains air handling units (no fuel). 
The FM's concern is that the access panel to get to the units would
allow the tenants to store things in there. The space is wood
construction and is approximately 20 ft long, 7 ft wide and 4.5 ft high.
There is CPVC pipe running through the space. The Blazemaster spec
states that sprinklers specifically listed for use with CPVC pipe shall
be used in combustible concealed spaces with their product.

The only sprinklers I can find that are listed for this use are COIN
sprinklers (Viking, Tyco). Since this space is over 3 ft high, COIN's
would not necessarily be required, per NFPA 13. Is there a non-COIN
sprinkler that is listed for protecting CPVC? I haven't been able to
find one.

Also, if this is area is to be considered accessible for storage, then
can CPVC pipe be in this space at all? Also, I don't believe the COIN
sprinklers can be used in a space that is considered occupied, n'est
pas?

Obviously, this building has already been piped and this is an
after-the-fact request by the FM.

Thoughts?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to