Reza,
Thanks for the info 

Brian Harris
FDFP INC.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili
Sent: Wednesday, November 14, 2007 12:55 AM
To: [email protected]
Subject: Re: FW: Maximum Velocity

 
  Brian,
  If you are talking about NFPA 13, I should say that NFPA 13 does not
specify a maximum limit for the calculated water velocity in any of the
pipes. The impact of high water velocities tends to be self-correcting. When
the velocity of water in a pipe is high, the pressure loss in that pipe is
also high. If the pressure loss is too high, the pipe size will be increased
to reduce the pressure loss, and the velocity will correspondingly go down.
  I suggest you also read this article.
  http://www.firesprinkler.org/techservices/articles/watervelocity.html
  I hope it is helpful.
  Regards,
  Reza
  
Brian Harris <[EMAIL PROTECTED]> wrote:
  


Regards,

Brian Harris

FDFP INC.



_____ 

From: Brian Harris [mailto:[EMAIL PROTECTED]
Sent: Monday, November 12, 2007 9:41 AM
To: '[email protected]'
Subject: Maximum Velocity


What's the general rule of thumb for maximum velocities in hydraulic calc's?
I use Hydra-Calc and the default is set @ 32, I assume that's feet per
second. Where did that number come from, I didn't see anything in the code
book. 


Regards,






_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

       
---------------------------------
Be a better sports nut! Let your teams follow you with Yahoo Mobile. Try it
now.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to