If this is a US Government job, it probably has to be from a domestic supplier......

At 04:07 PM 11/14/2007, you wrote:
Funny that this is an active thread again.  Just got a spec' for an Army
Housing project.   They call for a design in accordance with NFPA 13R,
and rack sprinklers per NFPA 230 with a maximum velocity of 20 FPS.
The real question here is where can I find out the country of origin of
the dope the EOR is smoking so that I can at least try to get on the
same page as the design team?

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, November 14, 2007 12:41 PM
To: [email protected]
Subject: Re: Maximum Velocity

also look at 13: A.22.4.1 (last sentence) It is not necessary to
restrict the water velocity when determining friction loss using the
Hazen-Williams formula.

This is also in the 02 edition.

Roland

On Nov 12, 2007, at 6:41 AM, Brian Harris wrote:

> What's the general rule of thumb for maximum velocities in
> hydraulic calc's?
> I use Hydra-Calc and the default is set @ 32, I assume that's feet per
> second. Where did that number come from, I didn't see anything in
> the code
> book.
>
>
> Regards,
>
>   <http://www.firstdefensefire.com/>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to