I have obtained documentation from the manufacturer of this EIFS exterior building finish system (artifical stucco) that it meets the the criterion of limited combustible condition (1) of NFPA13 2007 3.3.11. The problem I have is the condition (2) which states “materials, in the form and thickness used having neither a flame spread index greater than 25 nor evidence of continued progressive combustion, and of such composition that surfaces that would be exposed by cutting through the material on any plane would have neither a flame spread index greater than 25 nor evidence of continued progressive combustion when tested in accordance with NFPA 255 or ASTM E 84.”
I interpret this portion “ and of such composition that surfaces that would be exposed by cutting through the material on any plane would have neither a flame spread index greater than 25 nor evidence of continued progressive combustion when tested in accordance with NFPA 255 or ASTM E 84.” to be a part of condition (2) only. Will someone give me their understanding of this? Thanks, Ron Internal Virus Database is out-of-date. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)