I have a small building that is spec'd to have a deluge system with Ex Haz
Grp I for the sprinkler density.  The room is just under 5000 sq ft.  Since
this is going to be a deluge system, I have to flow every head in the area
with a design area of 5000 sq ft.  I want to "go up the curve" and have the
density of 0.20 gpm / sq ft over the most demanding 5000 sq ft.  

I don't see any reason why I can't do this, but just wanted to get some
input as to whether it is a good idea or not?  Some other things that come
about with the lower density is that I can stretch the sprinklers to 130 sq
ft instead of 100 sq ft and go up to 15' between sprinklers instead of 12'.
This will allow saving a couple sprinklers and branch lines in this area.

So, good idea or bad?  Anything I am missing?

Thanks in advance.

Travis 