This atrium is for a cancer center/clinic. I don't have any furniture
layouts but I am sure they will have some seating, information desk, etc....
This is also not a FM project. Any thoughts of the OH1 balconies for
elimination of buoyant smoke? 

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Thursday, December 27, 2007 10:27 AM
To: [email protected]
Subject: RE: Atrium

I can only suppose that the engineer is looking at FM Data Sheet 3-26,
table 11 and declaring the atrium (with the 0.45/2500 density) to be a
"heavily loaded area with or without plastics".  This Table identifies
FM's adjustment to design densities/areas in non-storage occupancies
based on high floor-to-ceiling spaces, in this case, ceilings 35 to 60
ft. above the floor.

Would you classify this atrium as heavily loaded (with combustibles)?

If it were "Lightly loaded" FM would require a 0.15/3000 design below a
35 to 60 ft. ceiling.

I believe the reasoning for the larger design areas/densities relates to
the delayed activation of sprinklers at those elevations, and the
subsequently larger fires they need to control.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Burtell
Sent: Thursday, December 27, 2007 9:31 AM
To: [email protected]
Subject: Atrium

I have an atrium/lobby where the engineer is asking for OH1 for the
balconies surrounding the atrium on first and second floors. There is no
glass separating the balcony from the atrium. Third floor balcony has LH
with a glass wall with Tyco window sprinklers only on the balcony side.
The
atrium ceiling has a .45/2500 with a max spacing of 10' x 10' using a
11K QR
ELO-231 sprinkler. This whole thing that was dreamed up is based on some
FM
data and is to control buoyant smoke in the atrium and the balconies. I
personally think it's wacked and overkill. I have PDF's of the engineers
concept drawings if anyone is interested. Is this a bad attempt to play
an
FPE? I am bidding this project and I would like to bring it back to
reality
and give some value engineering.

 

Joe Burtell, SET, CFPS

Burtell Fire Protection, Inc.

[EMAIL PROTECTED]

www.burtellfire.com

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to