There was also an article in FPC mag. and I believe it was also in sprinkler age on the effect of ceiling fans on water distribution.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Bill Minkel" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, January 30, 2008 2:13 PM
Subject: RE: 13 residential obstructions


In the same situation with a fan less than 8' from walls I was instructed
to use only one head per 2002 8.10.7.2.1.3, the four times rule I think,
since the residential sidewall could sprinkle both sides, above and below,
of the fan obstruction. So I did what I was told.

Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Tuesday, January 29, 2008 3:32 PM
To: [email protected]
Subject: RE: 13 residential obstructions

This thread reminds me of a dilemma I tussled with last week. In regards to
residential sidewalls, section 8.10.7.1.2 (02) says not to install
residential sidewalls within 8' of a light "or similar obstructions."  It
doesn't provide any exceptions, such as the light being only 4" deep and the
sidewall installed 6" down from the ceiling.  It simply says you can't do
it.

Is a soffit along the wall opposite the sidewall considered a "similar
obstruction"? I have a project where a 24" deep soffit is installed along 1
wall of the bedroom and along 1 wall of the living area (for ductwork).
Disregarding the soffits, sidewalls would work wonderfully.  If I consider
the soffit a "similar obstruction", that pretty much eliminates the use of
sidewalls.  Am I missing something?  Am I misinterpreting the intent of
8.10.7.1.2?

Ed Kramer
Littleton, CO


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to