We are working on a Dry Pipe Fire Sprinkler System for a Unheated Seed Corn 
Warehouse. The 1-1/2" small hose stations are to be connected to Wet Systems 
only according to the 2002 Edition of NFPA 13 - 8-16.5.1.4, therefore the 
Authority Having Jurisdiction is requiring a Class I Dry Standpipe in addition 
to the Dry Pipe Fire Sprinkler Systems based on 2002 Edition of NFPA 61 
-12-4.3.  A Fire Pump supplying the Fire Sprinkler Systems has a Test Header 
that is designed to be used as a hydrant on the exterior of the building. The 
warehouse is approximately 300' X 350'. 

Has anybody ran across this Class I Dry Standpipe requirement in a similar 
warehouse facility?

Thanks

Roger Scheidies
Bamford Inc. 