We are working on a Dry Pipe Fire Sprinkler System for a Unheated Seed Corn Warehouse. The 1-1/2" small hose stations are to be connected to Wet Systems only according to the 2002 Edition of NFPA 13 - 8-16.5.1.4, therefore the Authority Having Jurisdiction is requiring a Class I Dry Standpipe in addition to the Dry Pipe Fire Sprinkler Systems based on 2002 Edition of NFPA 61 -12-4.3. A Fire Pump supplying the Fire Sprinkler Systems has a Test Header that is designed to be used as a hydrant on the exterior of the building. The warehouse is approximately 300' X 350'.
Has anybody ran across this Class I Dry Standpipe requirement in a similar warehouse facility? Thanks Roger Scheidies Bamford Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)