Roland:
If the Committee is considering changes to the Res. / 3000 Sf application
area, would that come as a TIA to the 2007, or wait for the next full cycle?
I was talking to another committee member that thought it would move pretty
fast, to correct what they saw as a flaw.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Roland Huggins" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, February 06, 2008 9:14 AM
Subject: Re: residential heads in a 13 system
>
The same thing applies to the 3,000 sf remote area for unprotected
concealed combustible spaces. It does NOT apply to the residential
approach. Is that logical - NO. As a heads-up, that was mentioned at
the 13 meeting since it makes no sense but nothing has been done YET.
Roland