Occupancy is going to depend on quantity of materials in the room, both in storage and in use. Naptha is a Class II combustible and the Alcohol is a Class IB flammable. Table 307.7(1) in the IBC gives you the limits of chemicals allowed. In most cases the number can be doubled if there are sprinklers. Note that in "F-1" occupancies under 12,000 sq. ft., sprinklers are not required by the building code. If you're doing dispensing there are also issue in codes to deal with specific to that application.
If you exceed the permitted quantities in Table 307.7(1) then you end up in one of the class "H" occupancies. If that's the case then sprinklers become mandatory and there are a lot of other construction issues that the other disciplines will have to deal with as well. In a nutshell you need a complete Codes and Hazards analysis performed. Often people think just because the room is small, the effort to perform this kind of work should be simple. But special hazards type of environments can be quite complicated regardless of how big the room is. You need to know about the process, open or closed, dispensing, mixing, storage (and in storage you need to know how much, how high, in what, how much in process, etc.), building construction type, adjacent occupancies, and the list goes on. These studies are paramount to making sure you've selected the appropriate protection scheme. Also you need to check on local or state codes which may exceed the IBC or whatever the applicable code may be. Also see if there is an Insurance Underwriter for the owner. This is not meant to be a complete analysis, just a real brief overview. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregory Lindholm Sent: Tuesday, February 12, 2008 11:32 AM To: SprinklerFORUM Subject: Naptha & Isopropyl Alcohol I have been asked to quote a small project that will have some mixing & packaging of a product with isopropyl alcohol and aromatic 100 naptha. The storage tanks for these projects are located outside the building, with the liquids piped into the building. The "manufacturing room" for this is only 20' x 20', and the "packaging room" is 20' x 30'. The entire building is only 50' x 60'. Any thoughts from the forum? This is completely new for me. The GC is asking me if I knew if this building would be classified as "F" or "H" occupancy. (I know, these questions should be being taken care of by an engineer, but it has not gotten that far yet.) Greg Lindholm _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)