Occupancy is going to depend on quantity of materials in the room, both
in storage and in use.  Naptha is a Class II combustible and the Alcohol
is a Class IB flammable.  Table 307.7(1) in the IBC gives you the limits
of chemicals allowed.  In most cases the number can be doubled if there
are sprinklers.  Note that in "F-1" occupancies under 12,000 sq. ft.,
sprinklers are not required by the building code.  If you're doing
dispensing there are also issue in codes to deal with specific to that
application. 

If you exceed the permitted quantities in Table 307.7(1) then you end up
in one of the class "H" occupancies.  If that's the case then sprinklers
become mandatory and there are a lot of other construction issues that
the other disciplines will have to deal with as well.  

In a nutshell you need a complete Codes and Hazards analysis performed.
Often people think just because the room is small, the effort to perform
this kind of work should be simple.  But special hazards type of
environments can be quite complicated regardless of how big the room is.

You need to know about the process, open or closed, dispensing, mixing,
storage (and in storage you need to know how much, how high, in what,
how much in process, etc.), building construction type, adjacent
occupancies, and the list goes on.  

These studies are paramount to making sure you've selected the
appropriate protection scheme.  Also you need to check on local or state
codes which may exceed the IBC or whatever the applicable code may be.
Also see if there is an Insurance Underwriter for the owner.  

This is not meant to be a complete analysis, just a real brief overview.




Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregory
Lindholm
Sent: Tuesday, February 12, 2008 11:32 AM
To: SprinklerFORUM
Subject: Naptha & Isopropyl Alcohol

I have been asked to quote a small project that will have some mixing &
packaging of a product with isopropyl alcohol and aromatic 100 naptha.
The storage tanks for these projects are located outside the building,
with the liquids piped into the building. The "manufacturing room" for
this is only 20' x 20', and the "packaging room" is 20' x 30'. The
entire building is only 50' x 60'.

Any thoughts from the forum? This is completely new for me.

The GC is asking me if I knew if this building would be classified as
"F" or "H" occupancy. (I know, these questions should be being taken
care of by an engineer, but it has not gotten that far yet.)

Greg Lindholm
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to