That's as may be, but on high-rise buildings the code requires an emergency gen-set anyway, so once that's fait accompli the economics of the pump as a stand-alone line item generally favors the electric. Depending on size, it may favor electric a LOT - the wild card isn't the cost of the pump itself, but the size of the main panel and service on the electrical side. Once you get up and over 250 HP, it can be VERY expensive to feed the building (and can lead to a second transformer in SOME states and under the jurisdiction of SOME utilities) and a diesel starts to make sense again.
Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Friday, February 15, 2008 9:37 AM To: [email protected] Subject: RE: Diesel vs Electric We have found that a diesel pump alone is more cost effective than an electric with a gen set. Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Charles Thurston Sent: Friday, February 15, 2008 7:32 AM To: [email protected] Subject: Diesel vs Electric Hello sprinklerforum, I am looking for opinions on installing a Diesel fire pump Vs installing an Electric fire pump and Gen Set. I have a location that is being cut loose from the "Site Wide" fire pump loop now owned by others. -- Best regards, Charles mailto:[EMAIL PROTECTED] Coastal Fire Protection _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)