That's as may be, but on high-rise buildings the code requires an
emergency gen-set anyway, so once that's fait accompli the economics of
the pump as a stand-alone line item generally favors the electric.
Depending on size, it may favor electric a LOT - the wild card isn't the
cost of the pump itself, but the size of the main panel and service on
the electrical side.   Once you get up and over 250 HP, it can be VERY
expensive to feed the building (and can lead to a second transformer in
SOME states and under the jurisdiction of SOME utilities) and a diesel
starts to make sense again. 

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, February 15, 2008 9:37 AM
To: [email protected]
Subject: RE: Diesel vs Electric

We have found that a diesel pump alone is more cost effective than an
electric with a gen set.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Friday, February 15, 2008 7:32 AM
To: [email protected]
Subject: Diesel vs Electric

Hello sprinklerforum,

  I am looking for opinions on installing a Diesel fire pump Vs
installing
  an Electric fire pump and Gen Set. I have a location that is being
  cut loose from the "Site Wide" fire pump loop now owned by others.

-- 
Best regards,
 Charles                          mailto:[EMAIL PROTECTED]
Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to