The difference is between Hydrant in the street and Hydrant in the internal
yard of the premises just after the service connection.  

Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Tuesday, February 19, 2008 5:30 PM
To: [email protected]
Subject: Re: C-Factor for old piping

Dan,

Is the 40% difference before and after all the equipment you
mentioned, all before, or all after?

On Feb 19, 2008 7:02 AM, danarbel <[EMAIL PROTECTED]> wrote:
>
> Todd,
>
> Regarding the service connection - can't be simpler.
>
> Static Pressure in the Yard and in the Public Street.
>
> Flow hydrant in the Yard,
>
> Residual Pressure in another hyd in the Yard and in a Hydrant on the
Street.
>
>
> Static the same, Residual 40% difference.
>
> It is as simple as that.
>
> No use for C-Factor:  There are Valves, Strainer, Flowmetrer,  Backflow
> Presenter.
>
> Dan
>
>
> Dan Arbel
> Tel: 972-4-8243337
> Fax: 972-4-8243278
> M: 972-52-2810593
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
> - FPDC
> Sent: Tuesday, February 19, 2008 2:01 PM
> To: [email protected]
>
> Subject: RE: C-Factor for old piping
>
> Dan,
>
> How are you setting up the test for flowing inside the building? Have
> you tried running one of these as a hydraulic gradient and
> empirically determining the C factor? What pipe materials are being
> used? If what you are concluding is correct, then should we be using
> a C factor of 84 instead of 140 for underground calcs.
>
>
>
>
> At 06:33 AM 2/19/2008, you wrote:
>
> >I think I was misunderstood, because I raised two issues concerning the
> >reliability of the calculations and mfg data.
> >
> >A.      New systems and
> >B.      Old systems.
> >
> >NEW SYSTEMS:
> >
> >In tests made across new service connections I got pressure losses
ranging
> >from 30% to 45%.  Just last week on a brand new system I got 40% loss.
> >
> >Imagine a designer advising the principal that he can construct a
warehouse
> >with reliance on the public supply providing 910 gpm for sprinklers based
> >upon ample water from the Public Supply, all based on Public Supply
testing
> >on the street and hydraulic calculation.
> >
> >Then, after completing the system, test is made next to the Risers and it
> >appears at the design pressure there is only 600gpm available.
> >
> >The flow test was made inside the premises; residual pressure was
measured
> >both within the premises and in the street.
> >
> >The residual pressure within the premises was lower 40% from that on the
> >street.  All valves are open and there is no explanation based on Mfg
data
> >and any calculation.
> >
> >Now think about the liability of the people involved.
> >
> >
> >OLD SYSTEMS:
> >
> >A total different situation is the old pipe.  There I got loss of 75%.
> >
> >In one location there was a design of ESFR requiring 1750 gpm.  In order
to
> >get that the principal had to replace a pump and to install 1500-2000 gpm
> >pump.
> >
> >The test I made on behalf of Insurer proved that the mains can deliver
only
> >500gpm at the required pressure.
> >
> >In another location, 6" connection from a pump to risers, the demand was
> >1780 gpm at 110 psi.  The actual measured supply was 400 gpm at 110 psi.
> >
> >Dan
> >
> >
> >Dan Arbel
> >Tel: 972-4-8243337
> >Fax: 972-4-8243278
> >M: 972-52-2810593
> >-----Original Message-----
> >From: [EMAIL PROTECTED]
> >[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
> >Sent: Monday, February 18, 2008 8:15 PM
> >To: [email protected]
> >Subject: Re: C-Factor for old piping
> >
> >There are the two extremes Dan was originally talking about. Old pipes
> >with a 140 and old pipes with 40% degradation. Then you get the water
> >purveyor that won't let you touch his stuff at all or at best will
> >only allow flow testing at midnight (what percentage do you add to get
> >a decent picture of peak use?) and only if you capture the water and
> >process out the chlorine he put in it. Or he'll give you water data on
> >a 50s system that was done in 1986 from a hydrant somewhere close. Or
> >he'll model flow by computer since somehow his modeling data can
> >magically disspell all the concerns we've been talking about for the
> >past few days. And, by the way, running that program will take four to
> >six weeks. On top of that nobody from the A&E team is going to take
> >responsible charge and the GC who just accepted (verbal, not signed)
> >George's design/build proposal didn't do it until two days before
> >GEORGE was supposed to start and now George is holding up the project.
> >And somehow we manage to get out a product with a huge success rate in
> >spite of all that, public apathy, owner hostility and often spotty
> >maintenance. There are few days that pass when I'm not sure that
> >running a hot dog stand isn't a better idea.
> >
> >On 2/18/08, George Church <[EMAIL PROTECTED]> wrote:
> > > Only time I had a requirement that we felt was obscene to degrade an
> > > existing UG loop - the local AHJ wanted us to use like C=90 for 1960's
> (?)
> > > UG loop around a plant being rebuilt after roof collapse (snow).
> > >
> > > Part of our work included cutting out a section of te existing UG and
we
> > > left a piece of the existing sitting there for the AHJ to examine; it
> was
> > > clean as a whistle and he then, if memory serves me correctly, C=140
or
> at
> > > least something closer to reality (and not requiring a booster pump
> after
> > > the booster pump). Call it a flow test by visual examination:)
> > >
> > > glc
> > >
> > > -----Original Message-----
> > > From: [EMAIL PROTECTED]
> > > [mailto:[EMAIL PROTECTED] On Behalf Of Roland
> > > Huggins
> > > Sent: Monday, February 18, 2008 12:24 PM
> > > To: [email protected]
> > > Subject: Re: C-Factor for old piping
> > >
> > > agreed.  AS already stated by others,  old underground water supplies
> > > require a flow test to assign a reliable C value.  Let's not forget
> > > to assign a continued amount of degradation if the existing
> > > conditions are accepted verses designing to what is tested today.  I
> > > must confess not exactly sure what NFPA 24 says (if anything) since
> > > that memorized text is assigned to a portion of the memory bank that
> > > is not longer accessible.
> > >
> > > Roland
> > >
> > > On Feb 18, 2008, at 8:43 AM, [EMAIL PROTECTED] wrote:
> > >
> > > > We
> > > > certainly cannot go to the design standard as it is designing with
new
> > > > pipe.  So, what is the answer?
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> >
> >
> >--
> >Ron Greenman
> >at home....
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
> >
> >No virus found in this incoming message.
> >Checked by AVG Free Edition.
> >Version: 7.5.516 / Virus Database: 269.20.7/1285 - Release Date:
18/02/2008
> >05:50
> >
> >
> >No virus found in this outgoing message.
> >Checked by AVG Free Edition.
> >Version: 7.5.516 / Virus Database: 269.20.7/1285 - Release Date:
18/02/2008
> >05:50
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.516 / Virus Database: 269.20.7/1285 - Release Date:
18/02/2008
> 05:50
>
>
> No virus found in this outgoing message.
> Checked by AVG Free Edition.
> Version: 7.5.516 / Virus Database: 269.20.7/1285 - Release Date:
18/02/2008
> 05:50
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.516 / Virus Database: 269.20.7/1285 - Release Date: 18/02/2008
05:50
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.516 / Virus Database: 269.20.7/1285 - Release Date: 18/02/2008
05:50
 