We always do this even if it means that the first inspection is before a
year or a little after a year. Even when properly sloped and drained
after a trip there will be build up of water later. 


Rod DiBona
Vice President
Rapid Fire Protection
[EMAIL PROTECTED]
605-348-2342 ph
605-391-3553 cell

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Michael
O'Brian
Sent: Saturday, February 16, 2008 3:43 PM
To: SprinklerFORUM
Subject: Dry Sprinkler Tests

Here in the Midwest it has been pretty cold.  This week we looked into
two system freezups.  Both sites stated they did their dry-pipe trip
test and NFPA 25 yearly testing last week.

 

We have always encouraged the dry test to occur during the warmer months
and avoid November-March

 

Does anyone else do the same.  I think both of these freeze ups would
have not occurred if the testing took place in the summer?

 

Michael O'Brian

Code Savvy Consultants

www.codesavvyconsultants.com

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to