I was taught that a person in a sprinklered area should never be able to look 
into an unsprinklered area. That is the rule of thumb that coincides with the 
prescriptive rules in NFPA 13 of "protected throughout" unless omission of 
sprinklers is permitted. The area you described does not qualify for omission 
of sprinklers. 
   
  J. Scott Mitchell, P.E. 
  
Bob Knight <[EMAIL PROTECTED]> wrote:
  -----Original Message-----
From: [EMAIL PROTECTED] 
[mailto:sprinklerforum- [EMAIL PROTECTED] On Behalf Of Todd 
Williams - FPDC
Sent: Monday, February 18, 2008 5:08 PM
To: [email protected]
Subject: Re: Ceiling Void Space

If FM Global has anything to say about it, yes. There is a building 
in MA with several floors of this type of thing that FM wants 
protected. I gave them a quote for drawings (100% survey), but they 
didn't feel like burning my mortgage.

At 06:54 PM 2/18/2008, you wrote:
|------------------------------------------
|
|
| NONCOMBUSTIBLE SPACE
|___________________________________________
| X = sprinkler @ ceiling
| 10" DEEP X 8' LONG VOID
| B/TWN CEILINGS
|___________________________
|
|
NONCOMBUSTIBLE SPACE |
|
-----------------------------
X = sprinkler @ ceiling

If this picture turned out, would sprinklers be required to be place 
In the "void" between the upper and lower ceilings?
The materials are ACT ceiling above w/ a gyp board ceiling below. 
The soffit type structure is completely wrapped, and there are no 
Openings into the noncombustible space beyond.

Thank you,

Bob Knight, CET
(208) 495-2057
[EMAIL PROTECTED]
www.firebyknight.com


       
---------------------------------
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to