Oooh, a literalist! 
I think J Scott is referring to the "concealed" portion of the term
combustible concealed space. He means the area above a cloud needs heads,
etc, not the building across the street you can see thru the window.

Pretty good read, Todd, since you CAN see in the bathrooms if the
non-self-closing door is open.

Glc
Ps- please don't take any offense, non intended.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Tuesday, February 19, 2008 6:20 PM
To: [email protected]
Subject: Re: Ceiling Void Space

I guess that kills the idea of windows. Would this really apply for 
things like omitting sprinklers in hotel bathrooms but being able to 
see them from the hall or bedroom?

At 06:05 PM 2/19/2008, you wrote:
>I was taught that a person in a sprinklered area should never be 
>able to look into an unsprinklered area. That is the rule of thumb 
>that coincides with the prescriptive rules in NFPA 13 of "protected 
>throughout" unless omission of sprinklers is permitted. The area you 
>described does not qualify for omission of sprinklers.
>
>   J. Scott Mitchell, P.E.
>
>Bob Knight <[EMAIL PROTECTED]> wrote:
>   -----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:sprinklerforum- [EMAIL PROTECTED] On Behalf Of Todd
>Williams - FPDC
>Sent: Monday, February 18, 2008 5:08 PM
>To: [email protected]
>Subject: Re: Ceiling Void Space
>
>If FM Global has anything to say about it, yes. There is a building
>in MA with several floors of this type of thing that FM wants
>protected. I gave them a quote for drawings (100% survey), but they
>didn't feel like burning my mortgage.
>
>At 06:54 PM 2/18/2008, you wrote:
>|------------------------------------------
>|
>|
>| NONCOMBUSTIBLE SPACE
>|___________________________________________
>| X = sprinkler @ ceiling
>| 10" DEEP X 8' LONG VOID
>| B/TWN CEILINGS
>|___________________________
>|
>|
>NONCOMBUSTIBLE SPACE |
>|
>-----------------------------
>X = sprinkler @ ceiling
>
>If this picture turned out, would sprinklers be required to be place
>In the "void" between the upper and lower ceilings?
>The materials are ACT ceiling above w/ a gyp board ceiling below.
>The soffit type structure is completely wrapped, and there are no
>Openings into the noncombustible space beyond.
>
>Thank you,
>
>Bob Knight, CET
>(208) 495-2057
>[EMAIL PROTECTED]
>www.firebyknight.com
>
>
>
>---------------------------------
>Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to