Are you really seeing mostly doug fir?  In Pugetopolis it seems I mostly see  
"HemFir". I haven't seen market numbers.  Hemfir as I understand it is Western 
Hemlock and several of the true fir species.

Yours,

Bruce Verhei

 -------------- Original message ----------------------
From: "[EMAIL PROTECTED]" <[EMAIL PROTECTED]>
> Bob,
> 
> Your conclusion is correct, however I would double check the designation 
> of the SG for Douglas Fir.
> My reference book on this is "Modern Timber Engineering", and Table L in 
> that document shows the
> SG for Doug Fir as 0.51, which would mean your multiplier would be 1.25, 
> resulting in a maximum
> load of 250 pounds (200 x 1.25) in the configuration you described .
> 
> It's sort of interesting, in looking at the table I noted, there are 
> only two types of wood with an SG
> less than 0.35, and all of the others are larger, suggesting the values 
> in the tables are most likely to
> be increased when applying this modifier. The lower SG types are 
> Northern White Cedar (0.32),
> Western Red Cedar (0.34). 
> 
> PARSLEY CONSULTING
> Ken Wagoner, SET
> 760.745.6181 voice
> 760.745.0537 fax
> [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
> 
> 
> 
> Bob Knight wrote:
> > Good morning,
> > I was asked a question a couple of days ago about the specific gravity of
> > wood in relation to FIGURE 9.3.5.9.1.  I think I understand what is being
> > shown, but I would like verification.  The tables within this figure showing
> > through-bolts and lag screws in wood has a footnote that states the specific
> > gravity of 0.35 was used in the table.   It then states that a multiplier
> > can be used for other types of wood.  So, here in the west Douglas fir is
> > the wood of choice.  It has a specific gravity of 0.45.  If I grasp this
> > correctly, this allows me to use a multiplier of 1.17 to adjust the
> > allowable loads found in the figure.  For example a 1/2" through bolt in
> > wood with a length of 1-1/2" is allowed 200 lbs when using angle C.
> > Applying the multiplier increases that allowable load to 234 lbs.  Do I
> > understand this correctly?  Thanks for your help.
> >
> > Bob Knight, CET
> > (208) 495-2057
> > [EMAIL PROTECTED]
> > www.firebyknight.com
> >
> >
> > No virus found in this outgoing message.
> > Checked by AVG Free Edition. 
> > Version: 7.5.516 / Virus Database: 269.20.8/1287 - Release Date: 2/19/2008
> > 10:55 AM
> >  
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
> >   
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to