Lots of spruce from our northern neighbors to,

On Fri, Feb 22, 2008 at 11:11 AM,  <[EMAIL PROTECTED]> wrote:
>
>  Are you really seeing mostly doug fir?  In Pugetopolis it seems I mostly see 
>  "HemFir". I haven't seen market numbers.  Hemfir as I understand it is 
> Western Hemlock and several of the true fir species.
>
>  Yours,
>
>  Bruce Verhei
>
>
>
>   -------------- Original message ----------------------
>  From: "[EMAIL PROTECTED]" <[EMAIL PROTECTED]>
>  > Bob,
>  >
>  > Your conclusion is correct, however I would double check the designation
>  > of the SG for Douglas Fir.
>  > My reference book on this is "Modern Timber Engineering", and Table L in
>  > that document shows the
>  > SG for Doug Fir as 0.51, which would mean your multiplier would be 1.25,
>  > resulting in a maximum
>  > load of 250 pounds (200 x 1.25) in the configuration you described .
>  >
>  > It's sort of interesting, in looking at the table I noted, there are
>  > only two types of wood with an SG
>  > less than 0.35, and all of the others are larger, suggesting the values
>  > in the tables are most likely to
>  > be increased when applying this modifier. The lower SG types are
>  > Northern White Cedar (0.32),
>  > Western Red Cedar (0.34).
>  >
>  > PARSLEY CONSULTING
>  > Ken Wagoner, SET
>  > 760.745.6181 voice
>  > 760.745.0537 fax
>  > [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
>  > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>  >
>  >
>  >
>  > Bob Knight wrote:
>  > > Good morning,
>  > > I was asked a question a couple of days ago about the specific gravity of
>  > > wood in relation to FIGURE 9.3.5.9.1.  I think I understand what is being
>  > > shown, but I would like verification.  The tables within this figure 
> showing
>  > > through-bolts and lag screws in wood has a footnote that states the 
> specific
>  > > gravity of 0.35 was used in the table.   It then states that a multiplier
>  > > can be used for other types of wood.  So, here in the west Douglas fir is
>  > > the wood of choice.  It has a specific gravity of 0.45.  If I grasp this
>  > > correctly, this allows me to use a multiplier of 1.17 to adjust the
>  > > allowable loads found in the figure.  For example a 1/2" through bolt in
>  > > wood with a length of 1-1/2" is allowed 200 lbs when using angle C.
>  > > Applying the multiplier increases that allowable load to 234 lbs.  Do I
>  > > understand this correctly?  Thanks for your help.
>  > >
>  > > Bob Knight, CET
>  > > (208) 495-2057
>  > > [EMAIL PROTECTED]
>  > > www.firebyknight.com
>  > >
>  > >
>  > > No virus found in this outgoing message.
>  > > Checked by AVG Free Edition.
>  > > Version: 7.5.516 / Virus Database: 269.20.8/1287 - Release Date: 
> 2/19/2008
>  > > 10:55 AM
>  > >
>  > >
>  > > _______________________________________________
>  > > Sprinklerforum mailing list
>  > > [email protected]
>  > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  > >
>  > > To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  > > (Put the word unsubscribe in the subject field)
>  > >
>  > >
>  > >
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > [email protected]
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  >
>  > To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  > (Put the word unsubscribe in the subject field)
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to